Default Generator Question

Looking at a Honda eu2000i..... will it run my FEC-100, a couple table top steam tables, a small fan, radio, and some lights?
__________________
Grey Street BBQ Competition Team
(2) Humphrey's Battle Boxes
(2) Large Big Green Egg

Follow Grey Sreet BBQ on Facebook!
Dex is online now   Reply With Quote


Unread 08-12-2011, 01:38 PM   #2
big brother smoke
somebody shut me the fark up.


 
big brother smoke's Avatar
 
Join Date: 05-03-06
Location: Ventura, CA
Downloads: 0
Uploads: 0
Default

Yes, it can run my RV without using the AC, so you should be good to go. You may want to do the wattage math though.
__________________
Peace and Smoke,
BBS

https://www.bigpoppasmokers.com/stor...nufacturer=314

Powered by the West Coast Offense: Big Poppa Smokers and Simply Marvelous

"Walk with Us"
big brother smoke is offline   Reply With Quote


Unread 08-12-2011, 02:19 PM   #3
Ford
is Blowin Smoke!
 
Ford's Avatar
 
Join Date: 04-14-07
Location: Lakeland Florida
Downloads: 0
Uploads: 0
Default

elec steam tables can draw a fair amount. Add up the wattages.
__________________
Ford
Retired competition cook. BBQ mentor.
Ford is offline   Reply With Quote


Unread 08-12-2011, 04:07 PM   #4
Redheart
is one Smokin' Farker
 
Redheart's Avatar
 
Join Date: 07-03-09
Location: Burris Crossroads, GA
Downloads: 0
Uploads: 0
Default

W=V*A
Wattage = voltage times amperage
We know the wattage is 2K
and the voltage is or should be 110/120
this means
2000 = 120(A)
or
A = 2000/120
AMP = 16.6

So you cannot have more than 16.6 amps at peak. Usually peak is 10 to 20% more than continual service rating.

Add up the wattage or the amperage of what you want to put on the generator at one time. If it is less than the rating you are fine.

Remember that cordage also increases the amperage draw.

As Sean Connery says in "The Name of the Rose",
"So endeth the lesson."
__________________
"Red"
Redheart is offline   Reply With Quote


Unread 08-15-2011, 08:08 AM   #5
Dex
is one Smokin' Farker

 
Dex's Avatar
 
Join Date: 08-04-09
Location: Avon, IN
Downloads: 0
Uploads: 0
Default

Anyone know anything about Generac Generators? I picked this one up because it was only $399.... but I haven't even taken it out of the box.

I know its not going to be as quiet as the Hondas..... but its a little easier on the wallet!
__________________
Grey Street BBQ Competition Team
(2) Humphrey's Battle Boxes
(2) Large Big Green Egg

Follow Grey Sreet BBQ on Facebook!
Dex is online now   Reply With Quote


Unread 08-15-2011, 09:51 AM   #6
Trucky1008
is One Chatty Farker

 
Trucky1008's Avatar
 
Join Date: 05-26-08
Location: Omaha, NE
Downloads: 0
Uploads: 0
Default

Like Ford said the steam table pans will draw the most. The one's I have are 1200 watts, so they can eat up 10 amps each.
__________________
Don
Pork Patrol BBQ
[URL="http://www.porkpatrolbbq.com"]www.porkpatrolbbq.com[/

Jambo Backyard
Fast Eddy FEC100 X2
BGE- Large x2
Certified MOINK Ball Maker, 2008
KCBS Member and CBJ
Extreme BBQ Trailer 8.5' x 22'
Trucky1008 is offline   Reply With Quote


Unread 08-15-2011, 09:56 AM   #7
Redheart
is one Smokin' Farker
 
Redheart's Avatar
 
Join Date: 07-03-09
Location: Burris Crossroads, GA
Downloads: 0
Uploads: 0
Default

Quote:
Originally Posted by Dex View Post
Anyone know anything about Generac Generators? I picked this one up because it was only $399.... but I haven't even taken it out of the box.

I know its not going to be as quiet as the Hondas..... but its a little easier on the wallet!
Having owned both here is my input.

Generac's are not just louder than the Honda E series, they are LOUDER!. You need them in a bunker to quiet them down. If you plan on using them at an event or to power a trailer they will probably exceed the allowable db. of the sound ordinance.
If it is for emergency or construction use you will be O.K., but may present problems camping, vending or at events.

This was written from my experiences. If you want a quiet generator you need to get an electronic inverter style, like the Honda E series. There are several other companies that make them though I cannot attest to the quality.
__________________
"Red"
Redheart is offline   Reply With Quote


Unread 08-15-2011, 10:11 AM   #8
AUradar
Full Fledged Farker
 
Join Date: 06-02-10
Location: NW Florida
Downloads: 0
Uploads: 0
Default

Quote:
Originally Posted by Redheart View Post
W=V*A

So you cannot have more than 16.6 amps at peak. Usually peak is 10 to 20% more than continual service rating.
very important in choosing generators. Some generators quote their peak wattage and others quote their running wattage. You want to make sure you do the math using the running wattage.


also, if it has a heating element its going to suck the power.
AUradar is offline   Reply With Quote


Unread 08-15-2011, 10:45 AM   #9
Dex
is one Smokin' Farker

 
Dex's Avatar
 
Join Date: 08-04-09
Location: Avon, IN
Downloads: 0
Uploads: 0
Default

Ok, so my single table top steam table list on the back 1200 watts. However, I only have it set at 2 on the dial or maybe 3 at max. Does it still draw 1200 watts when it is that low?

EDIT:

Ok so I went ahead and made a list of what all I would run to see if a 2000 W generator would work. Here is what I come up with.

FEC-100
Provided Information: 5 Amps, 120 V
Calculated Informiation: 600 Watts

Steam table
Provided Information: 120 V, 1200 Watts... again, 1200 MAX with dial set at highest setting? I usually use 2 or 3 on the dial.
Calculated Information: 10 Amps ..... if calculated using the full 1200 Watts

Lighting - I use 3 thin 21" fluorescent lights that are linked together. I assume info is PER light.
Provided Information: 120 V, 16 Watts
Calculated Information: .133 Amps

Radio
Provided Information: 120 V, 250 W
Calculated Information: 2.1 Amps

Your thoughts?
__________________
Grey Street BBQ Competition Team
(2) Humphrey's Battle Boxes
(2) Large Big Green Egg

Follow Grey Sreet BBQ on Facebook!

Last edited by Dex; 08-15-2011 at 11:21 AM..
Dex is online now   Reply With Quote


Unread 08-15-2011, 11:46 AM   #10
Yakfishingfool
Babbling Farker

 
Yakfishingfool's Avatar
 
Join Date: 10-01-05
Location: Shokan, New York
Downloads: 0
Uploads: 0
Default

you sound over...by and amp or two, get the 3k.
__________________
Oh It'z BBQ!
6 Kayaks, a Carolina Skiff J16 - "Calusa Wanderer"
1 Weber Gold Series Grill
1 WSM 18,1 WSM 22
1 Weber performer, 1 Smokey Joe Platinum
1 XL Big Green Egg
1 FEC 100
KCBS Certified Judge #9079
Yakfishingfool is offline   Reply With Quote


Unread 08-15-2011, 11:57 AM   #11
PitRow
Full Fledged Farker
 
PitRow's Avatar
 
Join Date: 03-31-11
Location: Oregon
Downloads: 0
Uploads: 0
Default

The continuous duty rating of the eu2000i is only 1600 watts, so you're over by more than a few watts. At least at the ratings you give above.

The way to be sure would be to get a watt meter, and plug everything into it using your house power and see exactly how many watts you're using.

Something like this...
Amazon.com: Kill a Watt Meter: Everything Else@@AMEPARAM@@http://ecx.images-amazon.com/images/I/314Xry08unL.@@AMEPARAM@@314Xry08unL
__________________
Mike
Char-Broil Bandera | A-Maze-n smoker | Weber 18.5" OTS
My Blog: Life In Pit Row
PitRow is offline   Reply With Quote


Thanks from:--->
Unread 08-15-2011, 12:28 PM   #12
Dex
is one Smokin' Farker

 
Dex's Avatar
 
Join Date: 08-04-09
Location: Avon, IN
Downloads: 0
Uploads: 0
Default

Any response to my question about the 1200 Watts on the steam table if it is on a low setting? Thanks for the link on the Watt Meter.... Ill pick me up one.
__________________
Grey Street BBQ Competition Team
(2) Humphrey's Battle Boxes
(2) Large Big Green Egg

Follow Grey Sreet BBQ on Facebook!
Dex is online now   Reply With Quote


Unread 08-15-2011, 12:37 PM   #13
AUradar
Full Fledged Farker
 
Join Date: 06-02-10
Location: NW Florida
Downloads: 0
Uploads: 0
Default

Quote:
Originally Posted by Dex View Post
Any response to my question about the 1200 Watts on the steam table if it is on a low setting? Thanks for the link on the Watt Meter.... Ill pick me up one.
typically the way they limited the voltage in things like that is to run them through a potiementer (or reostat for larger draws). This creates a voltage divider using resisters. Problem here is when you turn it down, you don't change the input power, you just heat up a resistor to disspate that power you don't want. Its not like a propane regulator where you limit the flow of gas.

So no, you wouldn't change the draw when only running on "2".

The only way to really lower the temp and draw at the same time is to use a PWM and I doubt you have that on your system. Not unless you have electronic control on it.
AUradar is offline   Reply With Quote


Thanks from:--->
Unread 08-15-2011, 01:28 PM   #14
Dex
is one Smokin' Farker

 
Dex's Avatar
 
Join Date: 08-04-09
Location: Avon, IN
Downloads: 0
Uploads: 0
Default

So a 2400 watt generator would do it then? Im looking at this Yamaha as well

http://www.yamaha-motor.com/outdoor/...5/0/specs.aspx
__________________
Grey Street BBQ Competition Team
(2) Humphrey's Battle Boxes
(2) Large Big Green Egg

Follow Grey Sreet BBQ on Facebook!
Dex is online now   Reply With Quote


Unread 08-15-2011, 02:55 PM   #15
AUradar
Full Fledged Farker
 
Join Date: 06-02-10
Location: NW Florida
Downloads: 0
Uploads: 0
Default

Quote:
Originally Posted by Dex View Post
So a 2400 watt generator would do it then? Im looking at this Yamaha as well

http://www.yamaha-motor.com/outdoor/...5/0/specs.aspx
thats a 2000 watt generator.

again, run wattage and max wattage are not the same thing. You need to caculate for run wattage.

Keep in mind that different companies "size" their generators based on running and peak. So one company may rate that generator as 2400, another would rate it as 2000. Both are valid, but I think rating them as the peak power is very misleading.


based on your numbers, you need 17.233 run time amps. That generator is going to be maxed out, if it works. I would look for something bigger.
AUradar is offline   Reply With Quote


Reply

Similar Threads
Thread Thread Starter Forum Replies Last Post
Question about the soldering iron/tin can cold smoke generator colonel00 Q-talk 11 12-26-2011 07:19 PM
Honda generator question. moocow Q-talk 4 08-21-2011 10:32 PM
Generator? Mo-Dave Competition BBQ 26 02-04-2010 12:28 PM
Generator Question..... U2CANQUE Q-talk 21 02-04-2009 05:53 PM

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Loading



All times are GMT -5. The time now is 08:22 AM.


Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2014, vBulletin Solutions, Inc.
vBulletin Optimisation provided by vB Optimise v2.6.0 Beta 4 (Lite) - vBulletin Mods & Addons Copyright © 2014 DragonByte Technologies Ltd.
2003 -2012 © BBQ-Brethren Inc. All rights reserved. All Content and Flaming Pig Logo are registered and protected under U.S and International Copyright and Trademarks. Content Within this Website Is Property of BBQ Brethren Inc. Reproduction or alteration is strictly prohibited.
no new posts