contest trailers with ground problems
plow boy and me and jeff brinker when we plug in to an genorator at an contest our ground falts pop all the time
then this weekend brewmaster nate telles me to get ride of the ground and it will stop (it worked i had full power) didn't know if any others had this problem york
__________________
MOFO Chapter - BBQ Brethren KCBS CBJ - Beta Beta Que jim beam black coke |
|
04-29-2009, 08:31 PM | #2 |
somebody shut me the fark up.
Join Date: 10-09-06
Location: Blue Springs, MO
|
I don't know that I'd want to get rid of my ground with my electronics on board.
__________________
Pork Pullin Plowboys (and Smoke on Wheels) Save a hog, ride a plowboy! www.plowboysbbq.com Todd Johns (me); Blue Springs, MO Randy Hinck (PigBoy); Concordia, MO Andy Groneman (Hodedo); KC, KS (Cameo Appearances) FEC-500SS; FEC-100 (Right handed); FEC-100 (Left handed); Country Smoker Tailgater; Big Green Egg (2-large, small, mini); Cookshack Pellet Fired Charbroiler |
|
04-29-2009, 08:37 PM | #3 |
Full Fledged Farker
Join Date: 03-29-08
Location: Huron, SD
|
This happens because the grounds and the neutrals are tied together (paralleled). If you have an electrical panet in your trailer then they are probably all tied under the same ground bar. Because your trailer panel will always be subfed off of whatever you plug into these should be isolated.
|
|
04-29-2009, 08:38 PM | #4 |
Full Fledged Farker
Join Date: 03-29-08
Location: Huron, SD
|
By the way, getting rid of the ground is never a good idea, it's in there for a reason.
|
|
04-29-2009, 08:54 PM | #5 |
is one Smokin' Farker
Join Date: 10-15-06
Location: washington mo
|
have an electriction look at it and see what the problen is
york
__________________
MOFO Chapter - BBQ Brethren KCBS CBJ - Beta Beta Que jim beam black coke |
|
04-29-2009, 08:59 PM | #6 |
Full Fledged Farker
Join Date: 03-29-08
Location: Huron, SD
|
I'm an electrician, come and cook the contest in Huron, SD in early June and I'll fix it for free!
|
|
04-29-2009, 09:07 PM | #7 |
is one Smokin' Farker
Join Date: 10-15-06
Location: washington mo
|
an little to far from st louis
but thanks
__________________
MOFO Chapter - BBQ Brethren KCBS CBJ - Beta Beta Que jim beam black coke |
|
04-29-2009, 10:27 PM | #8 |
is One Chatty Farker
Join Date: 09-25-05
Location: Jefferson City, Missouri
|
Nate is right....We had the same problem in October at Bass Pro in Columbia. I think Nate's dad was having the same issue too.
__________________
"Please let me be the person my dog thinks I am." ~Author Unknown 8 x 18 Haulmark Trailer Fast Eddy FEC 100 Traeger Texas BBQ 075 UDS "Cool Hand Luke" 3 Weber Kettles and a Yellow Thermapen KCBS Certified BBQ Judge #8425 |
|
04-29-2009, 10:47 PM | #9 |
is One Chatty Farker
Join Date: 07-05-07
Location: St. Louis
|
|
|
04-30-2009, 08:34 PM | #10 |
On the road to being a farker
Join Date: 06-06-07
Location: Owensboro, KY
|
I had the same problem on a trailer we used to have. The problem that I found was that a neutral and ground wire were connected together in a junction box.
Due to the way the GFCI's work the ground and neutral wires have to be separated.
__________________
Big Tom Pigs-R-Us cooking team |
|
05-01-2009, 06:24 AM | #11 | |
is Blowin Smoke!
Join Date: 04-14-07
Location: Lakeland Florida
|
Quote:
For the original poster, don't play with safety. The cost may be higher than you want to pay in the long run.
__________________
Ford Retired competition cook. BBQ mentor. |
|
|
05-01-2009, 07:31 AM | #12 |
is One Chatty Farker
Join Date: 07-05-07
Location: St. Louis
|
First off, I am not an electrician, nor do I claim to know a lot about the subject. But this thread got me thinking about something. Everyone is worried about plugging into an outlet without a ground and they probably do it all the time without realizing it. I have even done it myself without thinking about it. The people who run generators at contests, unless they have a copper rod planted in the ground, are running ungrounded power. I was reading on a couple websites that they recommend 8' of copper rod to ground a generator. I have seen a lot of rigs doing this and wanted to give everyone a heads up.
Cheers, Nate |
|
05-01-2009, 07:37 AM | #13 | |
is one Smokin' Farker
Join Date: 05-21-07
Location: Moberly, Mo
|
Quote:
Actually you are totaly correct - if you are running ot a generator - there is no true ground. Plain in simple. Home generators that are a backup for your house power, will ahve a ground, because the ground is already installed.
__________________
Paydabill Lit & Loaded BBQ I remember a day when I hated pellets - 2 pellet cookers latter! CBJ - love judging KCBS - member for 4 years MOFO Chapter Super fast - BLUE Thermopen |
|
|
05-01-2009, 01:23 PM | #14 |
On the road to being a farker
Join Date: 03-19-09
Location: Huxley, Iowa
|
Nate, I am not an electrician either but I do now that what you said is not entirely accurate. When running a generator you do not have a "ground" connected, that is true. However the purpose of a "ground wire" running from your equipment is to protect you in case something shorts, or you have a faulty neutral wire. In a generator you still have this protection it just goes to the generator instead of the ground rod. That is why people have problems with GFCI's and generators. As stated above GFCI's do not like to have the neutral and grounds connected.
Big Mike's BBQ |
|
05-01-2009, 02:00 PM | #15 |
Full Fledged Farker
Join Date: 09-13-07
Location: Sugar Creek, MO
|
I am sort of an electrician, No license but i work with electricity on the job all the time. A GFCI will not work correctly on an ungrounded system and a portable generator is an ungrounded system. So if you are relying on a GFCI in a trailer to save your butt in case something gets wet than you are not completely protected. It may work it may not. You would have to have an external ground rod in the ground and have the ground wires in the panal completely seperate from the neutral wires in order for it to work. If you don't have the ground rod in the ground than nothing is grounded.
__________________
Large Spicewine Bandera Green UDS (UGD) Blue UDS (UBD) Homemade 18"/36" Grillzilla Lang 60, (RIP) Home Built Trailer (500gallon Oil drum).(RIP) |
|
Similar Threads | ||||
Thread | Thread Starter | Forum | Replies | Last Post |
Trailers? | backporchbbq | Q-talk | 4 | 03-20-2008 03:17 PM |
Trailers, Trailers and more Trailers. | BBQchef33 | Competition BBQ | 33 | 02-20-2007 02:03 AM |
Thread Tools | |
|
|