Default contest trailers with ground problems

plow boy and me and jeff brinker when we plug in to an genorator at an contest our ground falts pop all the time

then this weekend brewmaster nate telles me to get ride of the ground and it will stop (it worked i had full power)

didn't know if any others had this problem

york
__________________
MOFO Chapter - BBQ Brethren
KCBS CBJ - Beta Beta Que
jim beam black coke
beam boys bbq is offline   Reply With Quote




Old 04-29-2009, 08:31 PM   #2
Plowboy
somebody shut me the fark up.
 
Plowboy's Avatar
 
Join Date: 10-09-06
Location: Blue Springs, MO
Default

I don't know that I'd want to get rid of my ground with my electronics on board.
__________________
Pork Pullin Plowboys (and Smoke on Wheels)
Save a hog, ride a plowboy!
www.plowboysbbq.com

Todd Johns (me); Blue Springs, MO
Randy Hinck (PigBoy); Concordia, MO
Andy Groneman (Hodedo); KC, KS (Cameo Appearances)

FEC-500SS; FEC-100 (Right handed); FEC-100 (Left handed); Country Smoker Tailgater; Big Green Egg (2-large, small, mini); Cookshack Pellet Fired Charbroiler
Plowboy is offline   Reply With Quote


Old 04-29-2009, 08:37 PM   #3
Gerrit_Boys
Full Fledged Farker
 
Join Date: 03-29-08
Location: Huron, SD
Default

This happens because the grounds and the neutrals are tied together (paralleled). If you have an electrical panet in your trailer then they are probably all tied under the same ground bar. Because your trailer panel will always be subfed off of whatever you plug into these should be isolated.
Gerrit_Boys is offline   Reply With Quote


Old 04-29-2009, 08:38 PM   #4
Gerrit_Boys
Full Fledged Farker
 
Join Date: 03-29-08
Location: Huron, SD
Default

By the way, getting rid of the ground is never a good idea, it's in there for a reason.
Gerrit_Boys is offline   Reply With Quote


Old 04-29-2009, 08:54 PM   #5
beam boys bbq
is one Smokin' Farker
 
beam boys bbq's Avatar
 
Join Date: 10-15-06
Location: washington mo
Default

have an electriction look at it and see what the problen is

york
__________________
MOFO Chapter - BBQ Brethren
KCBS CBJ - Beta Beta Que
jim beam black coke
beam boys bbq is offline   Reply With Quote


Old 04-29-2009, 08:59 PM   #6
Gerrit_Boys
Full Fledged Farker
 
Join Date: 03-29-08
Location: Huron, SD
Default

I'm an electrician, come and cook the contest in Huron, SD in early June and I'll fix it for free!
Gerrit_Boys is offline   Reply With Quote


Old 04-29-2009, 09:07 PM   #7
beam boys bbq
is one Smokin' Farker
 
beam boys bbq's Avatar
 
Join Date: 10-15-06
Location: washington mo
Default

an little to far from st louis

but thanks
__________________
MOFO Chapter - BBQ Brethren
KCBS CBJ - Beta Beta Que
jim beam black coke
beam boys bbq is offline   Reply With Quote


Old 04-29-2009, 10:27 PM   #8
River City Smokehouse
is One Chatty Farker
 
River City Smokehouse's Avatar
 
Join Date: 09-25-05
Location: Jefferson City, Missouri
Default

Nate is right....We had the same problem in October at Bass Pro in Columbia. I think Nate's dad was having the same issue too.
__________________
"Please let me be the person my dog thinks I am." ~Author Unknown
8 x 18 Haulmark Trailer
Fast Eddy FEC 100
Traeger Texas BBQ 075
UDS "Cool Hand Luke"
3 Weber Kettles and a Yellow Thermapen
KCBS Certified BBQ Judge #8425
River City Smokehouse is offline   Reply With Quote


Old 04-29-2009, 10:47 PM   #9
Brewmaster
is One Chatty Farker
 
Brewmaster's Avatar
 
Join Date: 07-05-07
Location: St. Louis
Default

Quote:
Originally Posted by River City Smokehouse View Post
Nate is right....We had the same problem in October at Bass Pro in Columbia. I think Nate's dad was having the same issue too.
Well it works in a pinch when you have no other choice.
Brewmaster is offline   Reply With Quote


Old 04-30-2009, 08:34 PM   #10
Big Tom
On the road to being a farker
 
Join Date: 06-06-07
Location: Owensboro, KY
Default

I had the same problem on a trailer we used to have. The problem that I found was that a neutral and ground wire were connected together in a junction box.

Due to the way the GFCI's work the ground and neutral wires have to be separated.
__________________
Big Tom Pigs-R-Us cooking team
Big Tom is offline   Reply With Quote


Old 05-01-2009, 06:24 AM   #11
Ford
is Blowin Smoke!
 
Ford's Avatar
 
Join Date: 04-14-07
Location: Lakeland Florida
Default

Quote:
Originally Posted by Big Tom View Post
I had the same problem on a trailer we used to have. The problem that I found was that a neutral and ground wire were connected together in a junction box.

Due to the way the GFCI's work the ground and neutral wires have to be separated.
It drove me crazy and I finally paid an electrician to fix it. Started with the input to the panel, then the panel, and finally each outlet. Found one where wires were to close together and when plugged into a GFI it would cause a fault. Minor adjustment and no problems since.

For the original poster, don't play with safety. The cost may be higher than you want to pay in the long run.
__________________
Ford
Retired competition cook. BBQ mentor.
Ford is offline   Reply With Quote


Old 05-01-2009, 07:31 AM   #12
Brewmaster
is One Chatty Farker
 
Brewmaster's Avatar
 
Join Date: 07-05-07
Location: St. Louis
Default

First off, I am not an electrician, nor do I claim to know a lot about the subject. But this thread got me thinking about something. Everyone is worried about plugging into an outlet without a ground and they probably do it all the time without realizing it. I have even done it myself without thinking about it. The people who run generators at contests, unless they have a copper rod planted in the ground, are running ungrounded power. I was reading on a couple websites that they recommend 8' of copper rod to ground a generator. I have seen a lot of rigs doing this and wanted to give everyone a heads up.

Cheers,
Nate
Brewmaster is offline   Reply With Quote


Old 05-01-2009, 07:37 AM   #13
paydabill
is one Smokin' Farker
 
paydabill's Avatar
 
Join Date: 05-21-07
Location: Moberly, Mo
Default

Quote:
Originally Posted by Brewmaster View Post
First off, I am not an electrician, nor do I claim to know a lot about the subject. But this thread got me thinking about something. Everyone is worried about plugging into an outlet without a ground and they probably do it all the time without realizing it. I have even done it myself without thinking about it. The people who run generators at contests, unless they have a copper rod planted in the ground, are running ungrounded power. I was reading on a couple websites that they recommend 8' of copper rod to ground a generator. I have seen a lot of rigs doing this and wanted to give everyone a heads up.

Cheers,
Nate

Actually you are totaly correct - if you are running ot a generator - there is no true ground. Plain in simple. Home generators that are a backup for your house power, will ahve a ground, because the ground is already installed.
__________________
Paydabill
Lit & Loaded BBQ
I remember a day when I hated pellets -
2 pellet cookers latter!
CBJ - love judging
KCBS - member for 4 years
MOFO Chapter

Super fast - BLUE Thermopen
paydabill is offline   Reply With Quote


Old 05-01-2009, 01:23 PM   #14
Big Mike's BBQ
On the road to being a farker
 
Join Date: 03-19-09
Location: Huxley, Iowa
Default

Nate, I am not an electrician either but I do now that what you said is not entirely accurate. When running a generator you do not have a "ground" connected, that is true. However the purpose of a "ground wire" running from your equipment is to protect you in case something shorts, or you have a faulty neutral wire. In a generator you still have this protection it just goes to the generator instead of the ground rod. That is why people have problems with GFCI's and generators. As stated above GFCI's do not like to have the neutral and grounds connected.

Big Mike's BBQ
Big Mike's BBQ is offline   Reply With Quote


Old 05-01-2009, 02:00 PM   #15
pigpen269
Full Fledged Farker
 
pigpen269's Avatar
 
Join Date: 09-13-07
Location: Sugar Creek, MO
Default

I am sort of an electrician, No license but i work with electricity on the job all the time. A GFCI will not work correctly on an ungrounded system and a portable generator is an ungrounded system. So if you are relying on a GFCI in a trailer to save your butt in case something gets wet than you are not completely protected. It may work it may not. You would have to have an external ground rod in the ground and have the ground wires in the panal completely seperate from the neutral wires in order for it to work. If you don't have the ground rod in the ground than nothing is grounded.
__________________
Large Spicewine
Bandera
Green UDS (UGD)
Blue UDS (UBD)
Homemade 18"/36" Grillzilla
Lang 60, (RIP)
Home Built Trailer (500gallon Oil drum).(RIP)
pigpen269 is offline   Reply With Quote


Reply

Similar Threads
Thread Thread Starter Forum Replies Last Post
Trailers? backporchbbq Q-talk 4 03-20-2008 03:17 PM
Trailers, Trailers and more Trailers. BBQchef33 Competition BBQ 33 02-20-2007 02:03 AM

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


Forum Custom Search: Enter your Search text below. GOOGLE will search ONLY the BBQ Brethren Forum.
Custom search MAY not work(no display box) in some configurations of Internet Explorer. Please use compliant version of Firefox or Chrome.







All times are GMT -5. The time now is 07:37 AM.


Powered by vBulletin® Version 3.8.8
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
2003 -2012 © BBQ-Brethren Inc. All rights reserved. All Content and Flaming Pig Logo are registered and protected under U.S and International Copyright and Trademarks. Content Within this Website Is Property of BBQ Brethren Inc. Reproduction or alteration is strictly prohibited.
no new posts